I need to gauge the amount of UPS protection I need for the equipment I have. I have several dedicated circuits for the large spread of servers and network equipment I'm working with.

For example, one of the PowerEdge's has three redundant 320w power supplies, but how much draw will this have on an UPS, in terms of watts, amps and volt amps?

9 replies

by thechas

Remember that the rating on a power supply is it's maximum. You are likely drawing much less.

I recomend that you borrow a clamp on AC current meter, and verify what your equipment is drawing.

Then multiply the current by 150% and the length of time that you need standby power.

Your UPS has to have a high enough contiuous output power rating to supply that 150% current, and enough reserve capacity to supply power for the lenght of time needed in hours.

Example:
A 5 amp draw on a 120 volt line is 600 watts.
So, you would want continuous capacity of 900 watts.
If you need to keep the system up for 30 minutes, you need a 450VAH reserve capacity.

Since watts is the product of volts and amps, watts and VA are essentially the same term.

by timwalsh

The APC web site (www.apcc.com) has a pretty good selector tool for sizing an UPS appropriately.
You input your requirements (i.e. input/output voltages required, number of outlets required, rackmount or not, amount of room for growth (expressed as a percentage of total capacity), amount of required uptime (once battery kicks in), etc.); next you input the equipment that will be connected to the ups (if your equipment is name brand, you can input manufacturer and model, then add any specific peculiarities for your system (number of drives, type of drives, other peripherals installed, etc.); then APC will calculate the total (probable) amount of power required and recommend one (or several) solutions from their product line. Of course there is nothing to say that you can't take the answer APC gives you and go to a different vendor and see what they offer. Several other major UPS vendors offer similar tools. You just need to remember that the answer you get will not be 100% accurate for your particular situation (although I find the vendors generally err on the side of too much rather than too little).
Using one of these tools definitely saves time over going to each piece of equipment to be connected and determining what youthink will likely be the peak draw or basing your decision only on what the max draw will be based on power supply capacity(s).
Hope this helps.

by timthetoolman

Hi,

Also remember that although much equipment is rated for "office use" these days, not all of it is. It may be that you have equipment that requires air conditioning to remain in spec. And an unconditioned computer room will heat up very quickly even for your office rated equipment!

We configured our machines to immediately start shutting down (cleanly) when the power went off because the UPS's weren't sufficient to drive the AirCon as well.

Our machines weren't just hyped up PCs. Wehad DEC Alpha machines that weren't especially heat tolerant...

Cheers,
Tim.

by chocotechstuff

The UPS provides run time from depending on the number of battery installed and the UPS total load level. So if you want to extend the runtime, you could decrease the load or add battery pack.