I've got some cabling folks that will pulling all the data and phone lines for a new building my employer is building. They want to pull 70 CAT5 cables down a 100ft hallway and support them with J-Hooks. My concern is for the cables at the bottom of this pile, especially where a couple of the cables are pinched between the hook and the 60+ cables piled on top. I would prefer a cable tray be used to spread out the cables and lesson the weight on the bottom cables but they contend that the j-hooks are fine for the project. Can anyone give some info as to whether I should continue to be concerned or if I'm worrying for nothing. Any documentation to support would be very appreciated so I can present to upper managment for support of my concerns. Thanks in advance.

9 replies

by ann777

If they install enough j-hooks (I recommend every 3 feet versus the standard of every 4 to 5 feet), then essentially there won't be cable sag and you need not worry about the pressure on individual cables because their weight is evenly supported on the hooks placed every few feet.

If they attempt to install j-hooks spread more widely apart, then the cables will sag and may develop problems depending on other factors as well. Movement, interferance, etc. will affect cables if they are not supported adequately.

Here are some links:

http://www.trceng.com/networking/attics.htm

http://www.bicsi.org/AVForums/aca-1/dispatch.cgi/Publicforum/docProfile/100049/d19990525172344/No/t100049.htm

http://cr.ucdavis.edu/policies/cabling/cabtwo2.htm

http://www.barbershill.isd.esc4.net/cablingbus.html

http://www.advantagecareertraining.com/set/setinst.htm

Please remove any embedded spaces from the above links, when pasting into your browser.

by isys

Your building codes should specify either a cable tray or conduit. Check with your city/county building inspectors.

Have you brought this up to your superiors? Will they support your decision.

Your problems won't begin until about a year or so when the combined weight of the cables on top begin to deform the conductors inside the poly jackets.

by azhan_maj

I think you are right to worry about the proposed installation because that is not the proper installation practice.
With that installation you may find the network or telephone work fine but I'm afraid that the cable performance may be degraded and you may face difficulty in the future. Of course as far as the installation is concerned using J-Hook meet the installation intention but that is not a recommended practice. I believe cable tray or cable ladder would do a lot better that the J-Hooks.
As for the standard practice you may want to refer to TIA/EIA-569 - Commercial Building Standard for Telecommunications Pathways and Spaces

by cordell

Well, as others have pointed out, specifics like that are under local/state building codes as to if it meets "specs". But make sure the trunk is bundled together with cable ties at frequent intervals. If done properly 70 cables is not an oversized trunk. Also, while it may be late, make sure they are offering a warranty on their work. If they are offering a 5 year warranty on throughput, and they say it's not a problem, you are probably OK. Don't worry, you should be watching those guys like a hawk. For every perfectionist in that feild, there's also and idiot. Good luck.