As a person that maintains several UPS systems (1 is rated at 2400 Amp Hours) compiling the above answers togather comes very close. You need:
1. Total MAXIMUM current draw.
2. Normal total power outages.
3. An idea of the normal voltage supplied to the systems (at least hourly) on at least a one week period. This will determine how stable the power is.
4. If system is monitored, your (or tech) normal response time.
5. If system is not monitored give at least 24 hours backup time.
Results determine:
1. Unstable power - use battery filtered UPS.
2. Power problems (extended outages, no generator) - Large central UPS.
3. Total minimum required UPS supplied power (@120% of max).
4. How long could the server be down before it impacts the company?
5. What you want or need to accomplish drives what type of UPS system you want/need.
BTW - Equipment type does not drive the system power requirements, MAX current rating (on the UL label) does!