This one has me stumped...(sorry for the length)

We have recently moved the location of a graphic design studio from one large room to a smaller room on the same floor of the same building. The new room has recently been re-wired for both power and cat5 network cables. The equipment in the room is all set up in a similar way to how it was previously except it is now just a little more cramped.

The problem we have now is that our design monitors (all big and very expensive) are now intermittently flickering throughout the day and this is driving the designers mad...who in turn are driving me mad. The strange thing is that this is not going on all the time, an hour here and an hour there, and it is not affecting any standard monitors in the room at all.

I have tried turning off all equipment except one machine, the problem is still there. I have run power in from a different phase in the building, still the same problem. I have even disconnected the cat5 and it still is there.

My thoughs are that this is some type of electromagnetic interference from outside the room. There is a bakery below but they don't cook during the day and 2 brand new air-con units outside the building about 5 metres away.

If any one has any thoughts on a solution it would be greatly appreciated.

Cheers....Karl.

8 replies

by i_izhaut

I see this before. It is electrical equipment causing radio interference. Do not search network cables or power it is RF. Get a sheilded cord for a monitor. more expensive but worth it and see if it goes away. otherwise, you may need better sheilded monitors or to find what is turning on when the interfeerence starts and find how to sheil it RF.

by lumberjack

does your office use cordless phones - move them away from the PCs if so - or swap a couple for old fashioned curly cable ones and see if any difference

by jschein

Check the refresh rates for one.

If none of the above work for you, move one of the monitors to another area in the building on someone elses machine and have them use it for a few days... If it continues - bad monitor.

by paulp

You might also try a UPS which also regulates the voltage. I suspect it might not help.
If you can prove the monitors work fine in a different location, I would say it's up to YOUR BOSS to hire someone who can diagnose and correct the "environmental" issues, or move the users to a friendlier location, or tell the users to deal with it.

by thechas

Sounds like power line coupling.

In the office I used to have, we had a major power buss directly overhead. When equipment connected to the power buss ran, all the monitors would flicker.
It was a LOT easier to see on the large CADD monitors, but was present on all monitors if you looked closely.

A company named Perfection Mica makes several products for shielding from magnetic fields.
I don't believe that their standard monitor enclosures are large enough for your needs.

Chas

by richard_barsby

Hi I have just had the same problem at a large insurance company, this was caused by a large power cable in the ceiling void carrying 150A per phase.

Look for large cables and find out what powers on at the times of the interference. Lift motors if short periods aircon, compressors, any high power electrical appliance.

Rich

by lmayeda

I had a similar problem. I replaced the monitor and the new monitor started to flicker also. It turned out to be a small personal fan located close to the monitor... moved the fan a couple feet away ... no flicker. Could it be something like a refrigerator that you would not likely turn off but whose motor goes on and off to maintain the temperature? Is the new office closer to the airconditioning units than the old office and does it kick on/off corresponding to your flickering problem?

by paulkinsey

Aircon units sound most likely cause, check if these come on when the flickering starts, or check other high power equip nearby.