The trouble is... most of this stuff is completely irrelevant to you. UPS choice and sizing is on a per site basis.
I installed an APC Silcon 30kVA unit, with a load of approx 30% per phase. This gave over 90 minutes of runtime on battery, for all machines in my server room. Production critical machines were in a datacenter cage elsewhere.
My PBX, office NS, MX and switches were in another room, and connected to an APC Matrix 5kVA unit. Over 120 minutes of runtime there.
The rating plates on all of your machines are lying. These are the maximum power ratings, with some tolerance added too. It is highly unlikely that you will ever see whatever machine draw its maximum rated current.
For a server room, some sort of online, or online equivalent system is required. The Silcon is a Delta conversion unit, and I had no problems with it, beyond its first calibration.
When you are getting a unit installed, insist that the engineers do a load test on it, to ensure the UPS has been calibrated properly, and will give you the runtime expected (and indeed displayed) by the UPS.
Don't run your UPS over 75% capacity it is not polite. (You should really be looking at another unit if that is where you end up...)