Could anyone recommend a size and type of UPS to use on a Server Rack running Three medium size servers and a tape loader on one rack and on rack #2, Primarily switches, firewalls, and routers? I've talked to Multiple vendors but they keep trying to sell me overpriced UPS like symetra from APC.

11 replies

by cg it

APC are good UPS's. Yeah, they are expensive but with servers, if you have a power outage, the more time you have to safely shut down the servers until the power comes back on the better. Takes me about 2 minutes to shut down a couple of PDC BDC Exchange & ISA servers and a DMZ Web server [the web server only takes about 30 seconds to shut down] safely and with APC, they give me the time to do it. My routers don't loose configuration info with power off so I don't worry about them but I do the servers.

by cg it

See TheChas and Tim Walsh's answers! Tim has the best idea!!! and recommendation.

by jgranados

I agree. But is there an APC solution I could use without having to buy an expensive solution like the Symmetra. Would a 1400 120 volt do the job. If so, do I need one or multiples?

by thechas

I don't know if this will save you money in the long run.

Get an electrician to come in and measure the power draw on the AC feed to your servers.

Once you know the actual power draw, you can make an intelligent decision as to how big and how many UPSs you need.

Use the size tools at APC, Tripp-Lite, or Sola as if this were a stand-alone PC.

Then, decide if you need additional features.

One BIG advantage of a true server UPS is that it monitors the battery condition and allows you to hot swap batteries.

You should be able to use a standard UPS IF, you are willing to follow a strict preventative maintenance program.
The program will include replacing the batteries or the UPS every 3 to 5 years.
To determine the required interval, you need to test the UPS every 6 months.

The BIG question is: what is the impact to the organization if the servers go down?

Chas

by timwalsh

Symetra is way overkill for your environment.

Go to the APC website and check out their UPS selector.

(http://www.apc.com/template/size/apc/index.cfm)

Choose the Advanced UPS Selector.

You enter data such as the type and quantity of electronic equipment you want to protect and parameters such the the desired amount of "on-battery" time, amount of overhead for future growth, and requirements such as "rack-mount" and the selector will show you several models that will meet your requirements.

Take a look at the Smart-UPS line. There are rack-mount UPS starting at 750VA (should be more than sufficient for your rack with switches, firewalls, and routers), and going up to 3,000 VA (which you may need for your server rack depending on server configuration. I would suggest a separate UPS for each rack.

by alpha-male

In direct response to your question about the 1400s....

At one of our locations we have individual servers on 1400s, but the answer on if it would work is "it depends". The more load you put on the UPS, the faster its battery will drain and the faster your machines will go down (provided you;re offering enough juice just to run the machines). I think a 1400 wouldn't be enough for 3 servers and network equipment. I think I'd look at a pair of 3000s - one for each rack.

This article offers a little (simple) insight:

http://www.pcworld.com/howto/article/0,aid,109379,00.asp

The recommendation about using APC's power needs calculator is a great one. That tool is every simple to use and will get you exactly what you want and require.Just go to the apc website (www.apc.com) and go under the "Selectors" menu tab.

Good luck! Hope this helps.....

by tim.doyle

I run 1400's on single servers with maybe a router and/or switch thrown on as additional load. Compaq ML370GS servers...I get about 10-13 minutes run time in a power outage.

I ran through and did the advanced configuration with 3 Compaq DL 580 servers and a 50% load expansion capability...lowest cost solution was the Smart UPS 5000 rack mount for around $2700.

by joseph moore

Personally, I use the SmartUPS 3000 rack-mountable model. When fully populated by IBM Netfinity servers, I can have around 50-80 minutes of runtime.
Really!

by rvickers78

Well do you want something that will shut down the server when a outage occurs or just let them run until the battery's fail? Just imagine, your home on the weekend and the power fails at work. Corrupt data and others can stop the server from restarting. I had this happen to me cause I had 2 servers on a 1400 APC unit and it died after 10 min. 1 server wouldn't even come back up, had to rebuild it. Spend the money and get something you can rely on.

by wlbowers

As a licensed journeyman and 15year computer tech, there is no reason that you can't use the smart-ups line.

Look on the back of each piece of equipment and you will find a tag that will provide you with the wattage required to operate that pieceof equipment. It might also have the amperage requirements.

Example: 120v 4A 480w You want the number with the w or watts. If you only find the v and a multiply them for the watts.

It might not be in this order but it will be there. Note: APC refers to the above example as 480va

Write the devices and wattage required for each piece of equipment down.

Now start 3 columns. Put the server's wattage at the top.

You want a ups per server. This will provide the software shutdown capability.

Lets say the server is the above example.

Server 480va
Tape 120va
firewall 260va
total 860va

Using APC express UPS selector with a 10 minute runtime the gave me 3 options for a runtime of 8 to 58 minutes all under $1000.00 dollars.

Now shuffel your devices between the three columns and go to the selector with the totals.

I will be glad to help if you email me directly with the information.

Good Luck Lee