    We’ve been growing a lot over the past year and have gone from 2 Compaq Proliant 200 servers in a closet to 2 Compaq Proliant 1600, 2 Compaq Proliant 800, 2 Compaq proliant 200, and a couple custom built servers. We’ve moved them out of the small closet and into a bigger, central room (of course). Now we are looking into cooling options because leaving the door open is both not enough to keep it cool and a security risk. In speaking with a few cooling people, they have asked what is the total kW of my servers. How do I find this out? I assume it’s a measurment of heat that they give out over time, but I don’t know where to get this information or if it’s something I can just calculate. Any suggestions would be great! thanks,
    Ron

All Comments

  • Author
    Replies
    • #3548358

      kW required for cooling server room?

      by ann777 ·

      In reply to kW required for cooling server room?

      You need to total the power supply KW on each of your servers and on each of the other mechanical devices that may be running in the room. Modems, printers, monitors, etc. all of them have power supplies — add them up.

    • #3548322

      kW required for cooling server room?

      by avigil72 ·

      In reply to kW required for cooling server room?

      You are talking about two different things, one is heat, and the other is power you need for your equipment. If you want to know who much power you need, just check the power supply in your servers, monitors, equipment. There should be a number in KW (Kilo Watts) or KV (Kilo Vatios) Both mean the same thing. just add all these numbers and that is the estimated KW. Probably they need that, because heat depends on power consumed.

    • #3548270

      kW required for cooling server room?

      by maxwell edison ·

      In reply to kW required for cooling server room?

      Computer equipment generates heat, and that heat could be calculated by knowing the watts of the equipment. So the watts of the equipment will tell you more than simply the total power required. For an analogy, a 100 watt light bulb will generate 341.2 BTUs an hour.

      1 watt = 3.412 BTU / HR

      100 watts = 341.2 BTU / HR

      1000 watts (KW ? KiloWatt) = 3412 BTU / HR

      Add the watts of all the equipment in the room, multiply by the factor above, and you?ll have to total heat generated by that equipment.

      Good luck,

      Maxwell