Can a 100pr copper jell filled feeder be terminate to a punch block without a transistion splice??

12 replies

by c. hilbrandt

If this cable is installed where it can be exposed to electrical power faults and lightning, a primary protector is required by the NEC. Chances are that it is so you will need to first terminate in approved lightning protection. You can verify this under NEC article 800 Part C. Also, be sure to maintain the 50 foot rule for outside plant cable (Needs to terminated within 50' of the entrance point or be installed in metallic conduit). Hope this helps.........

by jorary

This cable is not expose to power lines and lightning, this is a buried backbone cable that connect rooms, do I need to splice the jell filled to air core before terminating to a punch block?

by jorary

This cable is not expose to power lines and lighting, this is a buried backbone cable that connect rooms, do I need or is it necessary to splice the jell filled cable to air core cable before terminating to a punch block?

by otl

No.
Use orange extract to clean the individual wires (get rid of the gel)and use 66 (not best), 110 or 7010 (better), or wire wrap (best) type connection blocks to ensure a good connection.
Although surge suppression type blocks are advisable, younever know what power may cross this cables path.

by otl

The surge suppression blocks are not always necessary (see answer #1)
Sorry still not fully awake!

by otl

answer YES, you do not need a transition splice. But do ground the sheath on one end to keep the RF/EMF interference to a minimum

by jorary

If splice not needed how can I stop the jell from escaping? Please provide manuals, codes or standards to verify.

by otl

Can not provide manuals (Bell / AT&T) proprietary information.
The Jell will stay in the cable because you route the end up to the connecting block and a good electricians (black plastic) tape wrapping or heat shrink tubbing will "clean up" the end where you stripped back the sheath.